DAE (Bus 0 Enclosure 1) is faulted

Hi All,

I need help on an urgent basis.

Issue: DAE (Bus 0 Enclosure 1) is faulted, we see this alert in Unisphere and also from the command line.Amber LED.png

Product model: VNX5300  ( UNIFIED )

Greater WC Availability:   ENABLED                                 

System Fault LED:          ON                     

Fault summary:

FRU                   SPA                        SPB

--------------------  -------------------------  -------------------------

Bus0 Enc1             Faulted        

I have referred to this article also but no help.

https://community.emc.com/docs/DOC-77760

All cablings look good.

 

Moderator

 • 

7.6K Posts

March 10th, 2020 10:00

Hello Charanz444,

In unisphere if you expand the tree under spa does it show you that anything is faulted?  If you look under SPA is it showing your SPS as faulted?  Also, if you look at the management of both SP’s is it showing the fault on both or just when logged in via a single SP?

Please let us know if you have any other questions.

March 13th, 2020 00:00

It shows faulted on both SPA and SPB

Moderator

 • 

7.6K Posts

March 17th, 2020 11:00

Hello Charanz444,

When you expand the tree in unisphere where is the fault showing?  Is it showing as the SP is faulted or the SPS?

Please let us know if you have any other questions.

March 17th, 2020 18:00

Hi,

When I expand DAE tree all look good but I found below from SP collects.

spa

Enclosure 1, DAE Fault LED status : ON
Peer LCC Fault
Expander Fault
LCC Fault
Fault Led Code: 0x00042400

================================

SPB

Enclosure 1, DAE Fault LED status : ON
Expander Fault
LCC Fault
Fault Led Code: 0x00042000

 

But, both of them in the DAE tree looks green. I think LCC B has gone bad here.

Isn't it?