Unsolved
1 Rookie
•
21 Posts
0
402
August 20th, 2023 06:56
R6515 A/B power not working
Hello
I'm trying to enable redundant power supply on my R6515 however there are issues.
As soon as I change the redundancy policy to A/B I get errors in IDRAC. I also see that both PSU continue to draw power.
The server is connected to both A and B power so I don't see what the problem is.
PSU 1 is connected to A power circuit. PSU 2 is connected to B power circuit.
When I did a test by pulling one of the PSU, the server rebooted so there does not seem to be any redundancy.



No Events found!
DELL-Charles R
Moderator
•
4.4K Posts
0
August 21st, 2023 14:51
Hello David,
On the Power Configuration try:
Redundancy Policy : A/B Grid Redundant
Set Hot Spare: Enabled
In Primary PSU assign: PSU1 or PSU2
Power Factor Correction: Disabled
SDeltaE
1 Rookie
•
21 Posts
0
August 21st, 2023 18:42
@Dell -Charles R
I gave this a try but the same error happens.
In the event logs it says power redundancy lost
SDeltaE
1 Rookie
•
21 Posts
0
August 21st, 2023 21:59
@Dell -Charles R Strange it says that you've replied to me 2 hours ago but I don't see your reply anywhere on here or via browserling except for the preview in my notifications
"Dell -Charles R replied to your comment: Hello David, Can you post image of the selections you used? Try selecting the other PSU, than you have selected now, for the Primary PSU. Try give the DRAC a reboot and check results ag"
Yes. I've tried everything including this. I just tried it again and dashboard showed this again.
I'm using the latest firmware on bios and IDRAC.
SDeltaE
1 Rookie
•
21 Posts
0
August 27th, 2023 08:24
@Dell -Charles R I'm still unable to see any replies including my own :(
I can confirm this issue via browserling again
https://www.browserling.com/browse/win10/chrome115/https://www.dell.com/community/en/conversations/rack-servers/r6515-ab-power-not-working/64e1b92912fff17cb996d791?commentId=64e3b015f70c0510d27a7ae4&replyId=64e4f7d0fae0db2daad644d5
Do you think you could solve this issue or should we close this thread and open a new one since it's bugged?
SDeltaE
1 Rookie
•
21 Posts
0
November 11th, 2023 13:16
Are the PSU identical with identical firmware? Yes
Are the PSU LED lit? Yes
Is the system still on original hardware? Has anything been added or removed?
It's original except for the ram. It had 512GB but I've since upgraded it to 1TB. I used the Dell Part AA783423 16x sticks.
But this seems to be an issue with the psus? I'm almost considering if I need to get the 1100w version? The 550w should be enough as I only use 150-300w but the theoretical max load could be a little more than 550w and maybe it's this that's causing the issue?
But it's still strange. I can't get it to just use one PSU. It always uses both even if primary is set
>Try updating the PSU firmware:
I've now done this but after changing to A/B the same issue occurs.
(edited)
SDeltaE
1 Rookie
•
21 Posts
0
November 28th, 2023 11:17
@DELL-Young E
That didn't work either. It gives this
SDeltaE
1 Rookie
•
21 Posts
0
November 29th, 2023 04:19
@DELL-Marco B
I've updated the bios and idrac to latest version.
Both of the PSU have part number 06V43GA00 with firmware
linux-tg
1 Rookie
•
15 Posts
0
September 24th, 2024 15:04
Hi,
We experience the same problem described above. I think more people will probably have this issue. Is it already known at Dell support?
This is with BIOS 2.15.2, iDRAC 7.10.70.00, and powersupplies on 00.31.50
I am able to boot on one powersupply though.
after booting on one PSU, i put the second PDU online. Then i pull the plug again. Then the machine is powered off..
(edited)
DELL-Charles R
Moderator
•
4.4K Posts
0
September 24th, 2024 17:45
Hello,
First try updating the firmware on the PSU:
LiteOn 550W PSU (PN: NCNFF, 034X1) Firmware Package : 00.33.50
https://dell.to/4dg34AF
IMPORTANT:
After a successful power supply firmware download, the managed system will turn off for a duration ranging from three to twenty minutes to continue updating the firmware. It is imperative not to disturb/restart manually the system, wait until the PSU FW update finishes. (Update time may vary depending on number of PSU for update, it may vary approximately from 10 mins to 20 mins.Margin should be added to ensure the Dell Update Package (DUP) is not interrupted. Once the firmware update is complete, the managed system will reboot automatically.
Have you had a chance to shut down and swap slots to see if the issue follows the PSU or stays in the slot?
Try your test of power up on one PSU, install the other then pull power with the PSU in each position:
PSU1 / PSU2
PSU2 / PSU1
See if pulling power from each one in each configuration has different results.
We want to see if the issue is related to one of the PSU or a slot.
Have you tried different power cables and power source?
Test with PSU2 as primary PSU and see if the result is the same or different.
Has any hardware been added or removed from original configuration?
linux-tg
1 Rookie
•
15 Posts
0
September 25th, 2024 13:50
Hi Charles,
Thank you for the pointers. I will update the firmwares and retry PSU reseating.
linux-tg
1 Rookie
•
15 Posts
0
September 26th, 2024 07:18
Hi Charles,
I have performed PSU swapping and pulling even with 2 PSU from another machine, no luck. But we figured out that the faling machine is Revision A01. We also have machines with revision A03 that do NOT have the problem.
command performed: dmidecode |grep -A4 "Base Board Information"
Failing machine:
Working machine:
I have a strong feeling we hit a Board issue here. What do you think?
(edited)
linux-tg
1 Rookie
•
15 Posts
0
September 26th, 2024 10:31
Ok, we found it. an IDRAC setting that made the server to power down when a PSU did not have power or is removed.
rob.morris
1 Rookie
•
2 Posts
0
October 28th, 2024 16:18
@linux-tg Hi. I have an identical problem to that which you were having. What was the iDRAC setting that made the server to power down when a PSU did not have power or is removed? Thanks
Rob
rob.morris
1 Rookie
•
2 Posts
0
October 29th, 2024 08:40
After many long hours trawling through every iDRAC setting, I finally found it: Configuration > System Settings > Alerts Configuration > Alerts > Alert Configuration > Power Supply > Actions
My setting here was originally set to "Power Off" on a critical event for the Power Supply. I have now set this to "No Action" and now it works as it should have done.
Hope this helps someone else who has set their dual power supplies to A/B Grid Redundant but their server shuts down when only one power supply is disconnected.