R440 reboots when UPS switches to battery power

Hello,

I have an R440 with two PSU both connected to a OR2200LCDRT2U UPS. When the UPS switches to battery power the R440 reboots. The R440 turns back on and works on UPS battery power, but there is the reboot at the time the UPS switches.

The other devices connected to the same UPS (i.e. a switch and a modem stay on and do not reboot).

For troubleshooting purposes I have tried to connect to the same UPS an older R420 (instead of the R440), and this does not reboot (i.e. stays on) when the UPS switches to battery power.

Could you please advise if there is any setting on the R440 that can be adjusted to prevent this behavior?

Moderator

 • 

4.6K Posts

October 31st, 2025 20:41

Hello,

 

This could possibly be caused by UPS waveform type: Many line-interactive UPS models (like the OR2200LCDRT2U) output a simulated sine wave when on battery. Dell PowerEdge servers with high-efficiency PSUs often require a pure sine wave during transfer. If the waveform is not pure sine, the PSU may briefly lose sync and trigger a reboot.

 

Example: simulated sine wave or pure sine wave

https://www.dell.com/community/en/conversations/poweredge-hardware-general/poweredge-r440-apc-ups-problem/647fa339f4ccf8a8de909a0c?commentId=647fa3c3f4ccf8a8de9beae0

 

Why R420 works but R440 doesn’t may be because the older servers (like R420) have less sensitive PSUs and tolerate simulated sine wave and longer transfer times. R440’s PSU design expects enterprise-grade UPS with true sine wave output and fast transfer (<4 ms).

 

My recommendations to check would be:

 

3 Apprentice

 • 

1.1K Posts

October 31st, 2025 19:46

I have seen variations of this over the years, and its a combination of the PSU tolerances and the UPS's wave forms (jagged,smooth), signal amplitude and timing. you could try playing with the Power Configuration settings in the idrac gui, but I dont see them making much difference. As a test, try leaving one PSU connected to a non-UPS power outlet

Rey
#Iwork4dell

1 Rookie

 • 

4 Posts

October 31st, 2025 20:04

@DELL-Rey G​ I will try with one PSU connected to a non-UPS outlet. But it eludes me how this would help… would the hope be that the non-UPS outlet could somehow keep the server running in the moment when the UPS is switching to battery power even if the UPS has already detected an outage?

(edited)

3 Apprentice

 • 

1.1K Posts

October 31st, 2025 20:08

kinda-sorta, just a test. I think there is a "notification" to the system that something happened to the power flow and it reacts differently. 

#Iwork4Dell