Dell R740XD2 – Fan speed locked at 75–100% despite iDRAC/Bios settings
Hey all,
We’re having trouble getting the fan speed on our R740XD2s into a manageable range — it seems stuck between 75% and 100% for all fans, no matter what we do.
Hardware setup:
Dell PowerEdge R740XD2
24 HDD's installed (30-35C)
3 × PCIe NVMe (Samsung P1725) (40C)
2 × 12-core Xeon Silver CPUs
OS/BOOT: Flatcar
The problem:
When booting and running Flatcar, our fans automatically ramp - and stay - at:
Fans 1–2: ~70–75% (14,400–14,500 RPM)
Fans 3–6: ~88–100% (18,000–18,240 RPM)
This is drawing excessive power and increasing our electricity bill noticeably.
Thermal & cooling configuration:
Thermal Profile Optimization: Minimum Power (Performance per Watt Optimized)
Fan Speed Offset: Low
Minimum Fan Speed in PWM: Default (37% PWM)
PCIe Airflow Settings: Mostly disabled, except Slot 5 set to Automatic (Airflow Controlled)
System Inlet Temp: 22 °C
System Exhaust Temp: 35–36 °C
Target Exhaust Temp Limit: 70 °C (Default)
Temperature readings (30 systems average):
CPU1: 60-70 °C
CPU2: 66-77 °C
System Board Inlet: 22-23 °C
System Board Exhaust: 35-37 °C
What’s odd:
If I install Ubuntu 22.04, run updates and load drivers (plus ipmitool
), the fans immediately drop to a much more reasonable range (35–50%), while keeping CPU temps below 77 °C. This was without drives installed, perhaps that also affects airflow quite a lot.
What I’ve tried:
Multiple
racadm
commands to set manual fan control - no avail.BIOS and iDRAC cooling settings (20+ combinations) - no avail.
Low power mode (drops PWM slightly and saves ~30W — not enough)
Ideal target:
CPU fans (1–2): 75–80%
PCIe fans (3–6): 50–60% (no need for 88-100%)
Controlled manually
Current status:
Manual commands via iDRAC or IPMI have no effect under Flatcar
Ubuntu works fine, so this seems related to how Flatcar interacts with Dell’s thermal management?
Unknown PCIe NVMe drives may be influencing airflow logic, but I can’t get fine-grained control
Anyone have clues on how to:
Get manual fan control working in this setup, or
Stop the system from forcing such high fan speeds?
Screenshots from iDRAC attached for reference.
Thanks in advance — any insights would be greatly appreciated!
DELL-Charles R
Moderator
•
4.5K Posts
0
August 11th, 2025 18:44
Hello,
There are just a few settings you can try. I think you may have already.
Custom Cooling Fan Options for Dell EMC PowerEdge Servers
https://dl.dell.com/manuals/common/customcooling_poweredge_idrac9.pdf?dgc=SM&cid=243907&lid=spr5090153920&linkId=123036317
It looks like you have found the cause of the issue being the Flatcar container as you tested with Ubuntu works fine.
Have you considered a BOSS, Boot Optimized Storage Subsystem, for the boot OS?
As of current Dell documentation, Flatcar Container Linux is not listed as a validated or officially supported operating system for the PowerEdge R740xd2 platform.
Dell Validated Operating Systems for PowerEdge R740xd2
According to Dell’s Supported Operating Systems list for PowerEdge R740XD , the following OSes are officially supported:
https://www.dell.com/support/home/en-us/drivers/supportedos/poweredge-r740xd
Flatcar is not included in this list, which means Dell does not validate or certify it for enterprise support on R740xd2 systems.