ISILON H600 Disk repalcement procedure
Hello Guys help me to replace the disk in H600.
we are pressing the sled button but the led does not turn off.
Lnn Location Device Lnum State Serial Sled
-------------------------------------------------------
8 Bay C3 /dev/da6 10 SMARTFAIL WFK2YFLD C
Quick response is highly appreciated.
No Events found!
Praveen.Singh
3 Apprentice
•
482 Posts
0
December 14th, 2024 18:56
Respond Guys ?
Dell-SapanaPrabhu
Moderator
•
4 Posts
0
December 16th, 2024 09:01
Hi Praveen,
Please check if any jobs are running kindly use the below command
#isi job status -v
If there is FlexProtect job running it will not allow to proceed with replacement
Praveen.Singh
3 Apprentice
•
482 Posts
0
December 16th, 2024 16:20
@Dell-SapanaPrabhu thanks for the info sapna but currenlty no job running and the issue is same from past 3 month we are unable to replace the disk in around 4 nodes.
1 Attachment
Screenshot 2024-12-16 215018.png
Dell-AviralGupta
Moderator
•
2 Posts
0
December 17th, 2024 20:28
Hi Praveen,
As flexprotect job is not running and disk is in smartfail state, please try stopfailing the disk and check if goes back to healthy state. Use below command for stopfail.
# isi devices drive stopfail C3 --node-lnn=8
If the disk goes back to healthy, monitor for next 24 hours. If not, please raise a case with Dell support to investigate further.
Thanks,
Aviral Gupta
Did I answer your query? Please click on ‘Mark as Accepted Answer’. ‘Thumbs up’ the posts you like!
#Iwork4Dell
Phil.Lam
3 Apprentice
•
608 Posts
0
December 19th, 2024 15:44
@Praveen.Singh , has to be in "replace" status first. Create SR to investigate why flexprotect did not run.
(edited)
Praveen.Singh
3 Apprentice
•
482 Posts
0
March 9th, 2025 18:55
sorry for the late response guys, it was fixed thanks, will share the full action plan shortly.