Dell Compellent sc4020 with sc200 shelf temps issue
Hello.
had alerts about the SC200 shelf about IO module temps , it shows randomly and disappears randomly.
the IO module was replaced and still the same .
any ideas?
thank you in advance.
No Events found!
DELL-Chris H
Moderator
•
9.4K Posts
1
June 9th, 2025 19:33
Lukehy247,
There a few things that could be causing this, here is some examples of what could be happening and how to address it:
False Positives from Environmental Sensors
Firmware Mismatch or Bug
Backplane or Midplane Issues
Power Supply or Fan Module Fluctuations
A couple things you can try are:
Ensure your SCv3020 is running the latest supported SCOS version for your environment.
You can check this via Dell Storage Manager or CLI.
Use DSM or CLI to review historical temperature logs:
show hardware health
show enclosure status
Power down the shelf (if possible) and reseat both I/O modules and SAS cables.
Ensure both modules are securely latched and that cables are not under tension.
Run a Diagnostic Test
Hardware → Enclosure → Run Diagnostics
Let me know what you see and if this helps.
lukehy247
1 Rookie
•
2 Posts
0
June 10th, 2025 13:56
@DELL-Chris H thank you.
it covers most things , its an SC4020 not SCV3020
tianchou
1 Rookie
•
93 Posts
0
June 29th, 2025 01:45
It is better to run some diag command at CLI mode.