Urgent! Emercency shutdown of CX3-80
We just had a power surge and now I have amber lights on my storage processors and various errors and warnings in Celerra Manager. I need to do an emergency shutdown of my CX3-80
Does anyone have the shutdown procedures for a cx3-80 / EMC NAS NS80
I need to halt the data movers and I am not sure if I can just use the Celerra Manager (select data movers > shutdown each data mover) or if I have to use the command line via putty
If anyone can help that would be great!
No Events found!
kelleg
4.5K Posts
0
February 6th, 2013 13:00
This is for the CX3-80 Array part - not sure about the NAS side:
The following is a Primus(R) eServer solution:
ID: emc142352
Domain: EMC1
Solution Class: 3.X Compatibility
Goal What is the correct procedure for powering down a CX3 and CX4 series arrays?
Fact Product: CLARiiON CX3 series
Fact Product: CLARiiON CX4 series
Fix
Follow these steps:
WARNING! Never turn off the power directly to the SPE chassis or the OS-Boot chassis by using any switches on the power supplies. Never unplug any of the AC cables going to the SPE or OS-Boot chassis to disconnect power.
Note
The only power switches that should be used to shut down a CLARiiON CX-series array (SPE/OS-boot chassis or DPE) are the power switches on the standby power supplies (SPS). The CX3-20, CX3-40, and CX3-80 SPE and CX 4 series SP chassis and OS-boot chassis are plugged into the SPS units. From the rear of the cabinet, the left power supply of each chassis (SPE and OS-Boot) is plugged into the left SPS and the right power supplies are plugged into the right SPS.