CX4 Disk Copying off to hot spare
Why is my disk copying off to the hot spare if there are no indications of a drive failure? Should I have the disk replaced that its copying off from?
No Events found!
Anonymous User
457 Posts
0
April 20th, 2012 07:00
Hi,
Usually proactive Hotspare (copying to Hotspare) happened when the drive is nearly failing., This need an investigation to check why proactive hotspare is happening..., I would request you to generate SP collects and open a chat with CLARiiON team to review the SP collects.
Regards,
Suman Pinnamaneni.
STAI
1 Rookie
•
81 Posts
0
April 20th, 2012 07:00
As I was reading your reply, the drive failed. I have opened a case with EMC and have a new drive on the way.
Storagesavvy
474 Posts
0
April 20th, 2012 10:00
If the drive reaches a certain level of errors, it will proactively copy the data to a new disk, and then fail the original drive. The proactive copy is much less overhead on the array/performance than a rebuild operation, as such proactive copy is preferred.